    Home A/C

    So last night and today the ac is blowing room temperature air. I checked the filter, air flow seems cooler in there and there's a lot of condensation. I probably need to call someone in WDM to come take a look. Any tips or referrals?
    Unit is 5 years old
    Thanks,
    Mike.

  2. #2
    Rookie
    Points: 12,840, Level: 34
    Level completed: 28%, Points required for next Level: 510
    Overall activity: 2.0%
    Achievements:
    Veteran10000 Experience Points

    Join Date
    Feb 2009
    Location
    Monticello, IA
    Posts
    391
    Points
    12,840
    Level
    34

    Re: Home A/C

    Sounds like the A coil is frozen up turn on the fan and not the A/C. After a couple of hours the coil should be thawed out and then you can turn the air back on. You might also need to clean the coil that is in the house as well.

  3. #3
    Speechless
    Points: 234,711, Level: 100
    Level completed: 0%, Points required for next Level: 0
    Overall activity: 24.0%
    Achievements:
    Veteran50000 Experience Points
    isuno1fan's Avatar
    Join Date
    Mar 2006
    Location
    Clive, Iowa
    Posts
    15,974
    Points
    234,711
    Level
    100

    Re: Home A/C

    What he said. If that all fails you likely have a refrigerant leak.

  4. #4
    All-Star
    Points: 22,621, Level: 46
    Level completed: 8%, Points required for next Level: 929
    Overall activity: 0%
    Achievements:
    10000 Experience PointsVeteran
    dtclones's Avatar
    Join Date
    Sep 2009
    Location
    Des Moines
    Posts
    1,629
    Points
    22,621
    Level
    46

    Re: Home A/C

    If the coil isn't frozen, you might have a faulty compressor or refrigerant issues (leak). I would definitely check the coil first. If that doesn't do it, I'd call who ever installed the system. Schaal came out to my place to fix a similar problem and it still doesn't work so I wouldn't recommend them.

  5. #5
    All-Star
    Points: 32,101, Level: 55
    Level completed: 14%, Points required for next Level: 949
    Overall activity: 2.0%
    Achievements:
    25000 Experience PointsVeteran

    Join Date
    Sep 2009
    Location
    Cabot, AR
    Posts
    1,553
    Points
    32,101
    Level
    55

    Re: Home A/C

    We had a refrigerant leak on a 5 year old system, Schaal charged $262 to recharge it, they claimed over the phone they would have to fix the leak and it would be cheaper to get a new system but it they agreed to a recharge when here...it has worked fine since but I would not reccommend them either based on how they handled it

  6. #6
    Hall-Of-Famer
    Points: 83,625, Level: 89
    Level completed: 94%, Points required for next Level: 125
    Overall activity: 1.0%
    Achievements:
    Veteran50000 Experience Points
    simply1's Avatar
    Join Date
    Jun 2009
    Location
    Salt Lake City
    Posts
    4,642
    Points
    83,625
    Level
    89

    Re: Home A/C

    I did turn it off for about an hour or so, will try to leave it longer and dig into the coils as well. At least I know who to avoid, hah.

  7. #7
    All-Star
    Points: 18,090, Level: 41
    Level completed: 5%, Points required for next Level: 860
    Overall activity: 1.0%
    Achievements:
    Veteran10000 Experience Points
    kcclones's Avatar
    Join Date
    Mar 2006
    Location
    Kansas City
    Posts
    1,614
    Points
    18,090
    Level
    41

    Re: Home A/C

    Another AC question...i get a different answer all the time it seems. is it better to leave the Fan ON or on AUTO?

  8. #8
    Rookie
    Points: 12,840, Level: 34
    Level completed: 28%, Points required for next Level: 510
    Overall activity: 2.0%
    Achievements:
    Veteran10000 Experience Points

    Join Date
    Feb 2009
    Location
    Monticello, IA
    Posts
    391
    Points
    12,840
    Level
    34

    Re: Home A/C

    You don't really need to have your fan on all the time when your A/C is on. Its actually something you can use when your basement is cool but your main floor is a little warm but you don't have the A/C on. It will pretty much just get the cooler air from your basement upstairs as long as you have a return in the basement.(which if you dont have one right before the return goes to the furnace you should put a vent you can close in ASAP) If you have it on all the time with the A/C you are just making your electric bill higher than it needs to be.

  9. #9
    Addict
    Points: 59,615, Level: 75
    Level completed: 72%, Points required for next Level: 435
    Overall activity: 2.0%
    Achievements:
    Veteran50000 Experience Points
    CyinCo's Avatar
    Join Date
    Mar 2006
    Location
    Clive, IA
    Posts
    5,295
    Points
    59,615
    Level
    75

    Re: Home A/C

    The coil being frozen can happen when the fan isn't running but the compressor is running. This usually happens when the relay outside by the condensing unit freezes in the "on" position. Go outside and see if the compressor is running even when the unit is switched to "off" from cool. If it is still running, that is bad and your coil will freeze up and eventually could break open and spill your charge.

    There should be a breaker panel near the condensing unit. Just switch it to off to turn off the compressor until service can be done.
    ISU Grad 1997.
    ISU Fan for Life.

    Not in CO anymore but I'm not changing my name :)

  10. #10
    Recruit
    Points: 5,246, Level: 21
    Level completed: 40%, Points required for next Level: 304
    Overall activity: 0%
    Achievements:
    Veteran5000 Experience Points

    Join Date
    Apr 2006
    Posts
    101
    Points
    5,246
    Level
    21

    Re: Home A/C

    Quote Originally Posted by simply1 View Post
    So last night and today the ac is blowing room temperature air. I checked the filter, air flow seems cooler in there and there's a lot of condensation. I probably need to call someone in WDM to come take a look. Any tips or referrals?
    Unit is 5 years old
    Thanks,
    Mike.
    I've had good luck with Central Iowa Mechanical in the past.

  11. #11
    Hall-Of-Famer
    Points: 83,625, Level: 89
    Level completed: 94%, Points required for next Level: 125
    Overall activity: 1.0%
    Achievements:
    Veteran50000 Experience Points
    simply1's Avatar
    Join Date
    Jun 2009
    Location
    Salt Lake City
    Posts
    4,642
    Points
    83,625
    Level
    89

    Re: Home A/C

    So I left the fan on, AC off last night and it cleared out any semblance of coolness and wetness through the air flow, but no cool air yet. On to the coils and I'll take the advice to check outside as well.

  12. #12
    Hall-Of-Famer
    Points: 83,625, Level: 89
    Level completed: 94%, Points required for next Level: 125
    Overall activity: 1.0%
    Achievements:
    Veteran50000 Experience Points
    simply1's Avatar
    Join Date
    Jun 2009
    Location
    Salt Lake City
    Posts
    4,642
    Points
    83,625
    Level
    89

    Re: Home A/C

    Freon was way low, so that's fixed. Now I have to hope it doesn't drop again and pay for a leak check.

  13. #13
    Rookie
    Points: 8,577, Level: 27
    Level completed: 72%, Points required for next Level: 173
    Overall activity: 0%
    Achievements:
    Veteran5000 Experience Points

    Join Date
    Apr 2006
    Posts
    350
    Points
    8,577
    Level
    27

    Re: Home A/C

    Quote Originally Posted by Hasbeen View Post
    I've had good luck with Central Iowa Mechanical in the past.
    I know the owners of Central Iowa Mechanical, good people, definitely give them a call.

  14. #14
    Pro
    Points: 62,539, Level: 77
    Level completed: 56%, Points required for next Level: 711
    Overall activity: 14.0%
    Achievements:
    Veteran50000 Experience Points
    azepp's Avatar
    Join Date
    Dec 2009
    Location
    Ankeny
    Posts
    3,040
    Points
    62,539
    Level
    77

    Re: Home A/C

    Quote Originally Posted by simply1 View Post
    So last night and today the ac is blowing room temperature air. I checked the filter, air flow seems cooler in there and there's a lot of condensation. I probably need to call someone in WDM to come take a look. Any tips or referrals?
    Unit is 5 years old
    Thanks,
    Mike.
    What brand is it?

  15. #15
    Addict
    Points: 59,615, Level: 75
    Level completed: 72%, Points required for next Level: 435
    Overall activity: 2.0%
    Achievements:
    Veteran50000 Experience Points
    CyinCo's Avatar
    Join Date
    Mar 2006
    Location
    Clive, IA
    Posts
    5,295
    Points
    59,615
    Level
    75

    Re: Home A/C

    Quote Originally Posted by simply1 View Post
    Freon was way low, so that's fixed. Now I have to hope it doesn't drop again and pay for a leak check.
    Refilling without repairing is pointless. It is supposed to be a sealed system. If refrigerant leaked once, it'll do the same again unless something has changed.
    ISU Grad 1997.
    ISU Fan for Life.

    Not in CO anymore but I'm not changing my name :)

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
  • Football
  • Iowa State vs. Northern Iowa
  • August 31, 2013
  • 07:00 PM

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19